A storage warehouse has 40,000 VA of general lighting. What demand load applies under the NEC 2020 or 2023?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12113
- A: 26,250 VA
Explanation
For warehouses the first 12,500 VA counts at 100 % and the rest at 50 % (Table 220.42 in 2020, Table 220.45 in 2023): 12,500 + 27,500 x 0.5 = 26,250 VA.