A commercial kitchen has three units rated 15, 4 and 2 kW. What demand applies under NEC 2020/2023 Table 220.56?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12112
- D: 19 kW
Explanation
Three units take 90 %: 21 x 0.90 = 18.9 kW. The result may not be below the two largest units, 15 + 4 = 19 kW, so 19 kW is used.