A restaurant has four kitchen units rated 12, 9, 6 and 3 kW. What is the NEC 2020/2023 feeder demand for this equipment?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12111
- C: 24 kW
Explanation
Four units take 80 % (Table 220.56): 30 x 0.80 = 24 kW. This exceeds the two largest units (12 + 9 = 21 kW), so 24 kW is used.