A 10,000 ft2 retail store is calculated under the NEC 2020 or 2023. What is the general lighting load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12110
- B: 19,000 VA
Explanation
Retail stores take 1.9 VA per ft2 (Table 220.12 in 2020, Table 220.42(A) in 2023): 10,000 x 1.9 = 19,000 VA.