Question 12109 of 966 · Washington 01 Journey Level Electrician Exam
Under the NEC 2020 or 2023 unit load table, what is the general lighting load for an 8,000 ft2 office?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 12109
- A: 10,400 VA
Explanation
Offices take 1.3 VA per ft2 in the 2020 and 2023 unit load table (Table 220.12 in 2020, Table 220.42(A) in 2023): 8,000 x 1.3 = 10,400 VA. The 3.5 VA value is from older editions.
More questions: Load Calculations
- 12110A 10,000 ft2 retail store is calculated under the NEC 2020 or 2023. What is the general lighting load?
- 12111A restaurant has four kitchen units rated 12, 9, 6 and 3 kW. What is the NEC 2020/2023 feeder demand for this equipment?
- 12112A commercial kitchen has three units rated 15, 4 and 2 kW. What demand applies under NEC 2020/2023 Table 220.56?
- 12113A storage warehouse has 40,000 VA of general lighting. What demand load applies under the NEC 2020 or 2023?
- 12114Under the NEC 2020 or 2023, what load is calculated for each 2-wire laundry branch circuit in a dwelling?