A three-phase 460 volt motor delivers 25 hp with an efficiency of 92 % and a power factor of 0.86. What is the actual line current (not the NEC table value)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13014
- B: 29.6 A
Explanation
Input power is 25 x 746 / 0.92 = 20,272 W, and I = P / (E x 1.732 x PF) = 20,272 / (460 x 1.732 x 0.86) = 29.6 A. Ignoring both efficiency and power factor gives 23.4 A; forgetting 1.732 gives 51.2 A.