A 3-phase 4-wire wye feeder has linear loads of 50 A on phase A, 40 A on phase B and 30 A on phase C. What is the approximate neutral current?

Exactly one answer is correct.

Show solution

Correct answer to question 13019

  • C: 17.3 A

Explanation

For a wye system, IN = square root of (A squared + B squared + C squared minus AB minus BC minus CA) = square root of (2,500 + 1,600 + 900 minus 2,000 minus 1,200 minus 1,500) = square root of 300 = 17.3 A. Subtracting the smallest from the largest (20 A) is the single-phase shortcut that does not apply here.