Question 13052 of 844 · Washington 01 Journey Level Electrician Exam
Six current-carrying 8 AWG THHN copper conductors are in one raceway at 30 °C ambient, and all terminations are rated 75 °C. What is the maximum ampacity that may be used for each conductor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13052
- D: 44 A
Explanation
The derated value from the 90 °C column is 55 x 0.80 = 44 A, while the 75 °C termination limit is 50 A. The lower of the two governs, so 44 A may be used.
More questions: Electrical Calculations
- 13053Three current-carrying 2 AWG THHN copper conductors are installed at 35 °C ambient and terminate on 75 °C rated lugs. What is the maximum load current the conductors may be used for?
- 13054A raceway contains two 3-phase, 4-wire wye circuits, and the loads are mainly electronic (nonlinear), so the neutrals count as current-carrying. Equipment grounding conductors are also present. What adjustment factor applies?
- 13055A raceway holds three 120 volt, 2-wire branch circuits, each with its own neutral, plus one equipment grounding conductor per circuit. How many current-carrying conductors are counted for adjustment?
- 13056A raceway contains three 120/240 volt, single-phase 3-wire multiwire circuits. The neutrals carry only unbalanced current. What adjustment factor applies to the conductors?
- 13057What is the allowable ampacity of 4/0 AWG XHHW aluminum conductors in the 75 °C column at 30 °C ambient with not more than three current-carrying conductors?
- 1305812 AWG copper UF cable (60 °C rated) is installed where the ambient temperature is 40 °C. What is its corrected ampacity?