A box contains four 12 AWG and two 14 AWG insulated conductors, 12 AWG equipment grounding conductors and a receptacle connected to the 12 AWG conductors. What minimum volume is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13066
- B: 19.75 cu in
Explanation
Conductors: 4 x 2.25 + 2 x 2.0 = 13.0 cu in; grounding conductors count once at the largest size, 2.25 cu in; the yoke counts twice at the size of the conductors connected to it, 4.5 cu in. Total 13.0 + 2.25 + 4.5 = 19.75 cu in.
More questions: Electrical Calculations
- 13067What is the volume listed in 314.16(A) for a 4 inch by 2-1/8 inch square metal box?
- 13068A 4 inch by 1-1/2 inch square box (21.0 cu in) has a plaster ring marked 3.6 cu in. What is the maximum number of 12 AWG conductors permitted if nothing else is in the box?
- 13069A box contains three 14 AWG insulated conductors that are spliced and terminated, two 14 AWG pigtails that originate and end inside the box, and one 14 AWG equipment grounding conductor group. What minimum volume is required?
- 13070Which volume allowance does 314.16(B) assign to each 6 AWG conductor?
- 13071A 4 inch by 1-1/2 inch octagonal box (15.5 cu in) will contain a fixture stud, four 14 AWG insulated conductors and one 14 AWG equipment grounding conductor. What volume is required, and does the box comply?
- 13072A 3 inch by 2 inch by 3-1/2 inch device box is rated 18.0 cu in. It holds a switch, two 14 AWG cables with grounds (4 insulated conductors) and internal clamps. How many additional 14 AWG insulated conductors may be added?