Question 13079 of 844 · Washington 01 Journey Level Electrician Exam
Three 4 AWG THHN (0.0824 sq in each) and one 8 AWG THHN (0.0366 sq in) are to be installed in EMT. Which is the smallest trade size permitted? (40 % areas: 3/4 in 0.213, 1 in 0.346, 1-1/4 in 0.598 sq in)
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13079
- C: 1 in
Explanation
Total area is 3 x 0.0824 + 0.0366 = 0.2838 sq in. This exceeds 0.213 sq in for 3/4 inch EMT but fits within 0.346 sq in for 1 inch EMT.
More questions: Electrical Calculations
- 13080What is the total cross-sectional area of six 10 AWG THHN (0.0211 sq in each) and three 8 AWG THHN (0.0366 sq in each) conductors?
- 130813/4 inch EMT has a 40 % fill area of 0.213 sq in and 14 AWG THHN has an area of 0.0097 sq in. How many 14 AWG THHN conductors are permitted when all conductors are the same size?
- 130821 inch EMT has a total internal area of 0.864 sq in. What is the maximum cross-sectional area of a single conductor installed in it?
- 13083A 25 hp, 460 volt, three-phase induction motor has a table full-load current of 34 A. What is the minimum ampacity of its branch-circuit conductors?
- 13084What minimum conductor ampacity is required for a 5 hp, 230 volt, single-phase motor? (Table full-load current 28 A.)
- 13085What is the full-load current from Table 430.250 for a 10 hp, 208 volt, three-phase induction motor, and the resulting minimum conductor ampacity?