Question 13080 of 844 · Washington 01 Journey Level Electrician Exam
What is the total cross-sectional area of six 10 AWG THHN (0.0211 sq in each) and three 8 AWG THHN (0.0366 sq in each) conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13080
- D: 0.2364 sq in
Explanation
6 x 0.0211 = 0.1266 and 3 x 0.0366 = 0.1098, for a total of 0.2364 sq in. Swapping the areas (6 x 0.0366 plus 3 x 0.0211) gives 0.2829 sq in, and adding just one of each conductor gives 0.0577 sq in.