Question 13086 of 844 · Washington 01 Journey Level Electrician Exam
A 20 hp, 460 volt, three-phase motor has a nameplate current of 26 A. Table 430.250 lists 27 A. What is the minimum branch-circuit conductor ampacity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13086
- B: 33.75 A
Explanation
Conductor sizing uses the table full-load current, not the nameplate value: 27 x 1.25 = 33.75 A. Using the nameplate gives 32.5 A, which is the most common error.
More questions: Electrical Calculations
- 13087A 15 hp, 460 volt, three-phase squirrel-cage motor (not Design B energy efficient) has a table full-load current of 21 A. Using an inverse time breaker at its maximum percentage and the next-higher-size allowance, what breaker may be used?
- 13088A 10 hp, 230 volt, three-phase motor has a table full-load current of 28 A. What is the maximum dual-element time-delay fuse size under the basic percentage of 430.52?
- 13089A 30 hp, 460 volt, three-phase motor has a table full-load current of 40 A. What is the maximum nontime-delay fuse size, using the next-higher-standard-size allowance?
- 13090What is the maximum setting, under the basic table percentage, of an instantaneous trip breaker for a 10 hp, 460 volt, three-phase squirrel-cage motor with a table full-load current of 14 A?
- 13091A motor has a nameplate full-load current of 24 A and a marked service factor of 1.15. What is the maximum rating of a separate overload device under 430.32(A)(1)?
- 13092A motor has a nameplate current of 40 A, a service factor of 1.0 and a temperature rise of 50 °C. What overload rating is required under the basic rule?