Question 13099 of 844 · Washington 01 Journey Level Electrician Exam

Why does the full-load current from Table 430.250, rather than the motor nameplate current, determine motor branch-circuit conductor ampacity for a general-purpose motor?

Exactly one answer is correct.

Show solution

Correct answer to question 13099

  • C: 430.6(A)(1) requires the table values for conductor and short-circuit device sizing

Explanation

430.6(A)(1) requires the table currents for ampacity and short-circuit and ground-fault protection, while separate overload protection is based on the nameplate current. The tables do not include the 125 % factor.

Next to question ›