Question 13100 of 844 · Washington 01 Journey Level Electrician Exam
A 25 kVA single-phase transformer has a 480 volt primary and a 240 volt secondary. What are the full-load primary and secondary currents?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13100
- D: 52.1 A primary, 104.2 A secondary
Explanation
Single-phase current is kVA x 1,000 / E: 25,000 / 480 = 52.1 A and 25,000 / 240 = 104.2 A. The 1.732 factor (30.1 A and 60.1 A) does not belong in a single-phase transformer calculation.
More questions: Electrical Calculations
- 13101What is the full-load secondary current of a 75 kVA, three-phase transformer with a 208Y/120 volt secondary?
- 13102What is the full-load primary current of a 75 kVA, three-phase transformer with a 480 volt delta primary?
- 13103A 45 kVA, three-phase, 480 volt primary transformer (1,000 volts or less) is protected on the primary side only. What is the maximum primary overcurrent device, using the next-higher-standard-size note?
- 13104A single-phase transformer steps 480 volts down to 120 volts. If the primary current is 10 A, what is the secondary current (ignoring losses)?
- 13105A transformer has a turns ratio of 20 to 1 and a primary voltage of 2,400 volts. What is the secondary voltage?
- 13106A balanced three-phase load draws 150 A per phase at 208 volts. What is the minimum transformer kVA required?