WAC 296-46B requires an outdoor service disconnecting means installed on or near a building to be within sight and within what distance of the building?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 14091
- C: 15 feet
Explanation
WAC 296-46B-230 permits the service disconnecting means outside within sight of and within 15 feet of the building served. When installed inside, the service raceway may extend no more than 15 feet inside the building.