After electrical equipment has been submerged in flood water, which devices must always be replaced under WAC 296-46B?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 14095
- A: Breakers, fuses, receptacles and switches
Explanation
WAC 296-46B-110 requires breakers, fuses, controllers, receptacles, switches, heaters and sealed devices that were submerged to be replaced. Other equipment must be replaced or reconditioned by the manufacturer.