A 120/240 volt service drop passes over a roof with a slope of 4 in 12. What is the minimum clearance above the roof permitted by the exception for sloped roofs?

Exactly one answer is correct.

Show solution

Correct answer to question 2004

  • C: 3 ft

Explanation

Where the voltage between conductors is 300 volts or less and the roof has a slope of 4 in 12 or greater, the clearance may be reduced to 3 ft. See 230.24(A) Exception No. 2.