Question 2014 of 844 · Washington 01 Journey Level Electrician Exam
What is the minimum size copper conductor permitted for an overhead service drop, other than for limited loads?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2014
- D: 8 AWG
Explanation
Overhead service conductors must not be smaller than 8 AWG copper or 6 AWG aluminum or copper-clad aluminum. Smaller conductors down to 12 AWG hard-drawn copper are allowed only for limited loads of a single branch circuit. See 230.23(B).