A commercial service supplies 120 A of continuous load and 40 A of noncontinuous load. What is the minimum ampacity of the service-entrance conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2021
- C: 190 A
Explanation
Service-entrance conductors must carry 125 percent of the continuous load plus 100 percent of the noncontinuous load. 120 A times 1.25 is 150 A, plus 40 A gives 190 A. See 230.42(A).