Question 2023 of 844 · Washington 01 Journey Level Electrician Exam
A service supplies a small commercial building, not a dwelling, with more than two branch circuits. What is the minimum service disconnect rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2023
- C: 60 amperes
Explanation
For installations other than one-circuit, two-circuit and one-family dwelling installations, the minimum service disconnect rating is 60 amperes. See 230.79(D).
More questions: Services and Service Equipment
- 2024What is the minimum rating of the service disconnecting means for a one-family dwelling?
- 2025Using the 83 percent rule of the 2020 and 2023 NEC, what minimum aluminum XHHW conductor at 75 degrees C is needed for a 200 A, 120/240 volt one-family dwelling service?
- 2026What is the minimum size aluminum conductor permitted for an underground service lateral serving a general load?
- 2027An overhead outside branch circuit spans 60 ft between supports. What is the minimum copper conductor size?
- 2028What is the minimum vertical clearance for overhead service conductors above a residential driveway when the voltage does not exceed 300 volts to ground?
- 2029Where must the service overcurrent device be located relative to the service disconnect?