Where must the service overcurrent device be located relative to the service disconnect?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2029
- A: Part of the service disconnect or immediately adjacent to it
Explanation
The service OCPD must be an integral part of the service disconnecting means or located immediately adjacent to it. See 230.91.