What must be done with a service GFPE system when it is first installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2036
- D: It must be performance tested on site, with a written record
Explanation
The GFPE system must be performance tested when first installed, by a qualified person using primary current injection per the manufacturer's instructions. A written record must be available to the AHJ. See 230.95.