Service drop conductors at 120/240 volts pass over only the overhang of a roof to terminate at a through-the-roof service mast. What is the minimum clearance above the overhang?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2034
- D: 18 in.
Explanation
The overhang exception allows 18 in. where not more than 6 ft of conductors, 4 ft horizontally, pass over the roof overhang and terminate at a through-the-roof raceway or approved support. The voltage between conductors must not exceed 300 volts. See 230.24(A) Exception No. 3.