Question 2030 of 844 · Washington 01 Journey Level Electrician Exam
What is the maximum ground-fault trip setting permitted for service GFPE?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2030
- C: 1200 A
Explanation
The maximum setting is 1200 A, and the maximum time delay is one second for ground-fault currents of 3000 A or more. See the setting provisions of 230.95.
More questions: Services and Service Equipment
- 2031Under the 2020 and 2023 NEC, where must the emergency disconnect for a one-family dwelling be installed?
- 2032In a 120/240 volt single-phase dwelling service rated 200 A, the 2020 and 2023 NEC allow the service conductors to be sized at what percentage of the service rating?
- 2033What may be attached to a service mast that supports a service drop?
- 2034Service drop conductors at 120/240 volts pass over only the overhang of a roof to terminate at a through-the-roof service mast. What is the minimum clearance above the overhang?
- 2036What must be done with a service GFPE system when it is first installed?
- 2037What is the minimum height of working space for service equipment rated 1000 volts or less?