In a 120/240 volt single-phase dwelling service rated 200 A, the 2020 and 2023 NEC allow the service conductors to be sized at what percentage of the service rating?

Exactly one answer is correct.

Show solution

Correct answer to question 2032

  • D: 83 percent

Explanation

Section 310.12 permits service and main feeder conductors for 120/240 volt dwelling services up to 400 A to have an ampacity of not less than 83 percent of the service rating. This replaced the former table method.