Correct answer to question 2031
- B: In a readily accessible outdoor location
Explanation
Section 230.85 requires an emergency disconnect for one- and two-family dwelling services at a readily accessible outdoor location so first responders can shut off power without entering the building. This requirement first appeared in the 2020 edition.