Question 2027 of 844 · Washington 01 Journey Level Electrician Exam
An overhead outside branch circuit spans 60 ft between supports. What is the minimum copper conductor size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2027
- C: 8 AWG
Explanation
For overhead spans of 1000 volts or less, copper must be at least 10 AWG for spans up to 50 ft and 8 AWG for longer spans, unless supported by a messenger. See 225.6(A).
More questions: Services and Service Equipment
- 2028What is the minimum vertical clearance for overhead service conductors above a residential driveway when the voltage does not exceed 300 volts to ground?
- 2029Where must the service overcurrent device be located relative to the service disconnect?
- 2030What is the maximum ground-fault trip setting permitted for service GFPE?
- 2031Under the 2020 and 2023 NEC, where must the emergency disconnect for a one-family dwelling be installed?
- 2032In a 120/240 volt single-phase dwelling service rated 200 A, the 2020 and 2023 NEC allow the service conductors to be sized at what percentage of the service rating?
- 2033What may be attached to a service mast that supports a service drop?