Correct answer to question 2026
- A: 6 AWG
Explanation
Underground service conductors must not be smaller than 8 AWG copper or 6 AWG aluminum or copper-clad aluminum. A smaller size is allowed only for limited loads such as a single branch circuit. See 230.31(B).