Ground-fault protection of equipment is required for a service disconnect rated 1200 A on which system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2059
- B: 480Y/277 volt, 3-phase, 4-wire solidly grounded wye
Explanation
GFPE applies to solidly grounded wye services of more than 150 volts to ground for each disconnect rated 1000 A or more. A 480Y/277 volt system is 277 volts to ground, while 208Y/120 volt is only 120 volts to ground. See 230.95.