A feeder conductor has an ampacity of 115 A and does not supply receptacles for portable loads. What is the largest standard OCPD permitted under the next size up rule?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3025
- A: 125 A
Explanation
Where the ampacity does not match a standard rating, the next higher standard rating may be used if it does not exceed 800 A. 115 A is not standard, so 125 A is the next higher rating. See 240.4(B) and 240.6(A).