Unless specifically permitted elsewhere, what is the maximum OCPD for 14 AWG copper conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3027
- C: 15 A
Explanation
The small conductor rule limits 14 AWG copper to 15 A regardless of its table ampacity. See 240.4(D).