What is the length limit for outside feeder tap conductors that terminate at a single OCPD that is part of or next to the building disconnect?

Exactly one answer is correct.

Show solution

Correct answer to question 3032

  • C: There is no length limit

Explanation

Outside taps of unlimited length are allowed if they are protected from physical damage, terminate at a single breaker or set of fuses that limits the load to their ampacity, and the OCPD is part of or adjacent to the disconnect. See 240.21(B)(5).