Question 3037 of 844 · Washington 01 Journey Level Electrician Exam
Arc energy reduction is required where the highest continuous current trip setting of a circuit breaker is at least what value?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3037
- C: 1200 A
Explanation
Where a circuit breaker is rated or can be adjusted to 1200 A or higher, a method to reduce clearing time such as an energy-reducing maintenance switch must be provided. A similar rule applies to fuses rated 1200 A or more. See 240.87 and 240.67.
More questions: Feeders and Overcurrent Protection
- 3039May an OCPD be placed in a grounded conductor?
- 3040Which statement about supplementary OCPDs is correct?
- 3041Unless specifically permitted elsewhere, what is the maximum OCPD for 10 AWG aluminum conductors?
- 3042How must a 25 ft feeder tap terminate?
- 3043What is the general rule for the location of OCPDs?
- 3044A building main disconnect, not the service disconnect, is rated 1200 A on a 480Y/277 volt system. What does the NEC require?