Question 3036 of 844 · Washington 01 Journey Level Electrician Exam
In a multi-tenant building, who must have ready access to the OCPDs protecting the conductors supplying a tenant space?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3036
- B: Each occupant, for the OCPDs serving that occupancy
Explanation
Each occupant must have ready access to all OCPDs protecting the conductors supplying that occupancy, unless the building has continuous building management supervision. See 240.24(B).
More questions: Feeders and Overcurrent Protection
- 3037Arc energy reduction is required where the highest continuous current trip setting of a circuit breaker is at least what value?
- 3039May an OCPD be placed in a grounded conductor?
- 3040Which statement about supplementary OCPDs is correct?
- 3041Unless specifically permitted elsewhere, what is the maximum OCPD for 10 AWG aluminum conductors?
- 3042How must a 25 ft feeder tap terminate?
- 3043What is the general rule for the location of OCPDs?