Question 3044 of 844 · Washington 01 Journey Level Electrician Exam

A building main disconnect, not the service disconnect, is rated 1200 A on a 480Y/277 volt system. What does the NEC require?

Exactly one answer is correct.

Show solution

Correct answer to question 3044

  • C: GFPE in accordance with 230.95

Explanation

Each building or structure main disconnect rated 1000 A or more on solidly grounded wye systems over 150 volts to ground needs GFPE per 230.95. Exceptions cover continuous industrial processes, fire pumps and cases where protection is provided elsewhere. See 240.13.

Next to question ›