What does selective coordination of OCPDs achieve?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3048
- C: It limits an outage to the faulted circuit or equipment
Explanation
Selective coordination localizes an overcurrent condition so that only the OCPD nearest the fault opens. Upstream devices stay closed and other loads keep power. See the definition in Article 100.