Question 4017 of 844 · Washington 01 Journey Level Electrician Exam
In a restaurant kitchen, which 125-volt, 20-ampere receptacles require GFCI protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4017
- C: All receptacles in the kitchen
Explanation
For other than dwelling units, 210.8(B) lists kitchens without limiting the rule to countertop receptacles. Every covered receptacle in the commercial kitchen therefore needs GFCI protection.
More questions: Branch Circuits, GFCI and AFCI
- 4018A 125-volt receptacle is installed on the roof of an office building for servicing a rooftop unit. What protection is required?
- 4019In a fitness center, which of the following areas requires GFCI protection for its 125-volt receptacles under 210.8(B)?
- 4022In a commercial building, which of the following areas is excluded from the garage and service bay GFCI requirement in 210.8(B)?
- 4023A receptacle in a commercial building is located in an unfinished basement area used for storage. Is GFCI protection required?
- 4024A 125-volt receptacle in an office break room is 4 ft from the break room sink. Is GFCI protection required?
- 4030Under the NEC 2020 and 2023, dwelling unit outdoor outlets on single-phase branch circuits rated 150 volts or less to ground require GFCI protection up to what branch circuit rating?