Question 4054 of 844 · Washington 01 Journey Level Electrician Exam
A 20-ampere branch circuit supplies only one bathroom of a dwelling. Which of the following may it also supply?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4054
- A: The lighting and exhaust fan in that same bathroom
Explanation
The exception to 210.11(C)(3) permits a 20-ampere circuit that supplies a single bathroom to also supply other equipment within that bathroom. It may not extend to outlets outside the bathroom.