How many receptacle outlets in a hotel guest room must be readily accessible when the remaining receptacles are located for convenient furniture placement?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4078
- A: At least two
Explanation
210.60(B) allows the total number of receptacles required by 210.52(A) in guest rooms to be placed for convenient permanent furniture layout. At least two receptacle outlets must remain readily accessible.