Question 4081 of 844 · Washington 01 Journey Level Electrician Exam
A single receptacle is installed on an individual 20-ampere branch circuit. What is the minimum rating of the receptacle?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4081
- B: 20 amperes
Explanation
210.21(B)(1) requires a single receptacle on an individual branch circuit to have an ampere rating not less than that of the branch circuit. A single 15-ampere receptacle on a 20-ampere individual circuit is not permitted.