Question 4088 of 844 · Washington 01 Journey Level Electrician Exam
A branch circuit supplies a continuous load of 16 amperes and no noncontinuous load. What is the minimum conductor ampacity before any adjustment or correction?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4088
- D: 20 amperes
Explanation
210.19 requires branch circuit conductors to have an ampacity of at least 125 percent of the continuous load plus 100 percent of the noncontinuous load. 16 A x 1.25 = 20 A.
More questions: Branch Circuits, GFCI and AFCI
- 4089A branch circuit supplies 24 amperes of continuous load and 6 amperes of noncontinuous load. What is the minimum standard overcurrent device rating?
- 4090For branch circuit sizing, a continuous load is one where the maximum current is expected to continue for how long?
- 4091When may a branch circuit overcurrent device be sized at 100 percent of the continuous load instead of 125 percent?
- 4094A multiwire branch circuit supplies receptacles in a dwelling. What does the NEC require at the point where the branch circuit originates?
- 4095A multiwire branch circuit in general may supply only which type of load?
- 4096How must the conductors of a multiwire branch circuit be identified in a panelboard?