When may a branch circuit overcurrent device be sized at 100 percent of the continuous load instead of 125 percent?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4091
- A: When the assembly and device are listed for 100 percent operation
Explanation
The exception to 210.20(A) permits sizing at 100 percent of the continuous load where the assembly, including the overcurrent device, is listed for operation at 100 percent of its rating. Standard breakers are not listed that way.