In which dwelling rooms is a switched receptacle NOT permitted as a substitute for the required wall-switch-controlled lighting outlet?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4099
- D: Kitchens and bathrooms
Explanation
The exception to 210.70(A)(1) allows switched receptacles in place of a lighting outlet in habitable rooms, but not in kitchens and bathrooms. Those rooms need an actual lighting outlet.
More questions: Branch Circuits, GFCI and AFCI
- 4100A dwelling interior stairway has eight risers between floor levels. Where are wall switches required for the stairway lighting?
- 4101A dwelling attic contains a furnace that requires servicing. What lighting outlet is required?
- 4102For a dwelling, which of the following is NOT considered an outdoor entrance for the required exterior lighting outlet?
- 4103A 12 AWG copper THHN conductor has a 90 C ampacity of 30 amperes in Table 310.16. What is the maximum overcurrent protection generally permitted for it?
- 4104What is the ampacity of a 6 AWG copper THWN conductor in the 75 C column of Table 310.16?
- 4105A 30-ampere branch circuit terminates on equipment whose terminals are not marked with a temperature rating. Which column of Table 310.16 must be used to select the conductor?