Question 4105 of 844 · Washington 01 Journey Level Electrician Exam

A 30-ampere branch circuit terminates on equipment whose terminals are not marked with a temperature rating. Which column of Table 310.16 must be used to select the conductor?

Exactly one answer is correct.

Show solution

Correct answer to question 4105

  • B: 60 C

Explanation

110.14(C)(1)(a) requires terminations for circuits rated 100 amperes or less, or for 14 AWG through 1 AWG conductors, to use the 60 C column unless the equipment is listed and marked for a higher temperature. Unmarked terminals therefore limit the conductor to the 60 C ampacity.