Question 4108 of 844 · Washington 01 Journey Level Electrician Exam
When 90 C rated THHN conductors are installed with 75 C terminations, what is the 90 C ampacity used for?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4108
- D: As the starting value for adjustment and correction factors
Explanation
110.14(C) allows conductors with higher temperature ratings to use their higher ampacity for ampacity adjustment, correction or both. The final result may not exceed the ampacity at the termination temperature.
More questions: Branch Circuits, GFCI and AFCI
- 4109How may a 10 AWG grounded conductor be identified?
- 4110A 2 AWG grounded conductor has black insulation. How may it be identified as the grounded conductor?
- 4112A white conductor in a cable assembly is used as an ungrounded conductor for a switch loop. What does the NEC require?
- 4001In a dwelling unit, GFCI protection is required for all 125-volt through 250-volt receptacles installed in which of the following locations?
- 4002A receptacle in a dwelling unit bedroom is installed 5 ft from the top inside edge of the bowl of a bar sink. Is GFCI protection required?
- 4003In a dwelling unit, receptacles within what distance of the outside edge of a bathtub or shower stall require GFCI protection?