Question 4107 of 844 · Washington 01 Journey Level Electrician Exam

For a circuit rated over 100 amperes with conductors larger than 1 AWG, which temperature column may be used for termination purposes unless equipment is marked otherwise?

Exactly one answer is correct.

Show solution

Correct answer to question 4107

  • D: 75 C

Explanation

110.14(C)(1)(b) permits conductors for circuits rated over 100 amperes, or larger than 1 AWG, to be used at their 75 C ampacity. Higher values apply only when the termination is listed for them.

Next to question ›