Question 4106 of 844 · Washington 01 Journey Level Electrician Exam

An 8 AWG copper THHN conductor connects to terminals rated 75 C on both ends. What ampacity may be used for the circuit?

Exactly one answer is correct.

Show solution

Correct answer to question 4106

  • A: 50 amperes

Explanation

8 AWG copper is 40 A at 60 C, 50 A at 75 C and 55 A at 90 C. The 90 C insulation does not help because the 75 C terminals limit the conductor to 50 A under 110.14(C).

Next to question ›