Question 4102 of 844 · Washington 01 Journey Level Electrician Exam
For a dwelling, which of the following is NOT considered an outdoor entrance for the required exterior lighting outlet?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4102
- C: A vehicle door in a garage
Explanation
210.70(A)(2) requires a wall-switch-controlled lighting outlet on the exterior side of outdoor entrances or exits with grade-level access. A vehicle door in a garage is not considered an outdoor entrance or exit for this rule.
More questions: Branch Circuits, GFCI and AFCI
- 4103A 12 AWG copper THHN conductor has a 90 C ampacity of 30 amperes in Table 310.16. What is the maximum overcurrent protection generally permitted for it?
- 4104What is the ampacity of a 6 AWG copper THWN conductor in the 75 C column of Table 310.16?
- 4105A 30-ampere branch circuit terminates on equipment whose terminals are not marked with a temperature rating. Which column of Table 310.16 must be used to select the conductor?
- 4106An 8 AWG copper THHN conductor connects to terminals rated 75 C on both ends. What ampacity may be used for the circuit?
- 4107For a circuit rated over 100 amperes with conductors larger than 1 AWG, which temperature column may be used for termination purposes unless equipment is marked otherwise?
- 4108When 90 C rated THHN conductors are installed with 75 C terminations, what is the 90 C ampacity used for?