In a 120/240-volt, 3-wire multiwire branch circuit, why must the two ungrounded conductors be connected to opposite lines?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4097
- C: So the neutral carries only the unbalanced current
Explanation
On opposite lines, the neutral carries only the difference between the two line currents. If both ungrounded conductors were on the same line, the neutral would carry the sum of both currents and could be overloaded.
More questions: Branch Circuits, GFCI and AFCI
- 4098In a dwelling living room, what may substitute for the required wall-switch-controlled lighting outlet?
- 4099In which dwelling rooms is a switched receptacle NOT permitted as a substitute for the required wall-switch-controlled lighting outlet?
- 4100A dwelling interior stairway has eight risers between floor levels. Where are wall switches required for the stairway lighting?
- 4101A dwelling attic contains a furnace that requires servicing. What lighting outlet is required?
- 4102For a dwelling, which of the following is NOT considered an outdoor entrance for the required exterior lighting outlet?
- 4103A 12 AWG copper THHN conductor has a 90 C ampacity of 30 amperes in Table 310.16. What is the maximum overcurrent protection generally permitted for it?