A multiwire branch circuit in general may supply only which type of load?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4095
- B: Line-to-neutral loads
Explanation
210.4(C) limits multiwire branch circuits to line-to-neutral loads. Exceptions permit a single piece of utilization equipment or circuits where all ungrounded conductors open simultaneously by the overcurrent device.